Warm water enters a cooling tower at 34°C at a mass flow rate of 59.3 kg/s. The air entering at state 1 has h₁ = 54.2 kJ
-
- Site Admin
- Posts: 899603
- Joined: Mon Aug 02, 2021 8:13 am
Warm water enters a cooling tower at 34°C at a mass flow rate of 59.3 kg/s. The air entering at state 1 has h₁ = 54.2 kJ
Warm water enters a cooling tower at 34°C at a mass flow rate of 59.3 kg/s. The air entering at state 1 has h₁ = 54.2 kJ/kg da and w₁ = 0.009 kg v/kg da. The air leaving the cooling tower at state 2 has h₂ = 106.3 kJ/kg da and w₂ = 0.029 kg v/kg da. The make up water is supplied at 25°C and the mass flow rate of dry air is 46 kg da/s. What is the temperature of the cooled water leaving the tower? Express your answer in °C.