- Warm Water Enters A Cooling Tower At 34 C At A Mass Flow Rate Of 57 8 Kg S The Air Entering At State 1 Has H 54 6 Kj 1 (113.39 KiB) Viewed 32 times
Warm water enters a cooling tower at 34°C at a mass flow rate of 57.8 kg/s. The air entering at state 1 has h₁ = 54.6 kJ
-
- Site Admin
- Posts: 899603
- Joined: Mon Aug 02, 2021 8:13 am
Warm water enters a cooling tower at 34°C at a mass flow rate of 57.8 kg/s. The air entering at state 1 has h₁ = 54.6 kJ
Warm water enters a cooling tower at 34°C at a mass flow rate of 57.8 kg/s. The air entering at state 1 has h₁ = 54.6 kJ/kg da and w₁ = 0.007 kg v/kg da. The air leaving the cooling tower at state 2 has h₂ = 104.6 kJ/kg da and w₂ = 0.027 kg v/kg da. The make up water is supplied at 25°C and the mass flow rate of dry air is 45.2 kg da/s. What is the temperature of the cooled water leaving the tower? Express your answer in °C.