Business, Finance, Economics, Accounting, Operations Management, Computer Science, Electrical Engineering, Mechanical Engineering, Civil Engineering, Chemical Engineering, Algebra, Precalculus, Statistics and Probabilty, Advanced Math, Physics, Chemistry, Biology, Nursing, Psychology, Certifications, Tests, Prep, and more.
Post Reply
answerhappygod
Site Admin
Posts: 899603
Joined: Mon Aug 02, 2021 8:13 am

OUTSIDE AIR 90 F db, 74 F wb CHILLED WATER SUPPLY 5000 cfm CHILLED WATER COIL RETURN AIR DAMPER M 58 F db, 56 F wb ROOM

Post by answerhappygod »

Outside Air 90 F Db 74 F Wb Chilled Water Supply 5000 Cfm Chilled Water Coil Return Air Damper M 58 F Db 56 F Wb Room 1
Outside Air 90 F Db 74 F Wb Chilled Water Supply 5000 Cfm Chilled Water Coil Return Air Damper M 58 F Db 56 F Wb Room 1 (20.47 KiB) Viewed 20 times
. Controls are set in the A/C chilled water supply coils so that25% of outside air is mixed with 75% return air in the cooling coilbox as shown in the diagram below. Find the A/C load on the chilledwater coils for the outside air supplied as shown, to supply 20,000cfm air-conditioned air to the room. [. Find the mixed air enthalpyand the enthalpy of the chilled air, then use an air conditioningequation. Answer: About 26 Tons.]
OUTSIDE AIR 90 F db, 74 F wb CHILLED WATER SUPPLY 5000 cfm CHILLED WATER COIL RETURN AIR DAMPER M 58 F db, 56 F wb ROOM 20000 cfm VENTILATION