Consider a one-phase transformer rated at 15 MVA, 14/2 kV and 50
Hz.
It goes through a short-circuit test with |V1|=14 kV applied on
the primary side. During the test, the primary side draws rated
current and 6 MW.
Calculate the current drawn on the primary side during the test
and cosfi.