#6 (20 pts): A 20 MVA, 13.8 kV generator has the following data: Subtransient reactance 0.25 per unit. Negative Sequence
-
answerhappygod
- Site Admin
- Posts: 899604
- Joined: Mon Aug 02, 2021 8:13 am
#6 (20 pts): A 20 MVA, 13.8 kV generator has the following data: Subtransient reactance 0.25 per unit. Negative Sequence
#6 (20 pts): A 20 MVA, 13.8 kV generator has the following data: Subtransient reactance 0.25 per unit. Negative Sequence reactance: 0.35 per unit Zero Sequence reactance: 0.1 per unit. Internal voltage Ex = 1.0 per unit Calculate: 1. Subtransient current in the generator 2. Symmetrical components of the voltage Vao, Val and Vaz from point a to ground