Business, Finance, Economics, Accounting, Operations Management, Computer Science, Electrical Engineering, Mechanical Engineering, Civil Engineering, Chemical Engineering, Algebra, Precalculus, Statistics and Probabilty, Advanced Math, Physics, Chemistry, Biology, Nursing, Psychology, Certifications, Tests, Prep, and more.
Post Reply
answerhappygod
Site Admin
Posts: 899603
Joined: Mon Aug 02, 2021 8:13 am

#6 (20 pts): A 20 MVA, 13.8 kV generator has the following data: Subtransient reactance 0.25 per unit. Negative Sequence

Post by answerhappygod »

6 20 Pts A 20 Mva 13 8 Kv Generator Has The Following Data Subtransient Reactance 0 25 Per Unit Negative Sequence 1
6 20 Pts A 20 Mva 13 8 Kv Generator Has The Following Data Subtransient Reactance 0 25 Per Unit Negative Sequence 1 (35.92 KiB) Viewed 11 times
#6 (20 pts): A 20 MVA, 13.8 kV generator has the following data: Subtransient reactance 0.25 per unit. Negative Sequence reactance: 0.35 per unit Zero Sequence reactance: 0.1 per unit. Internal voltage E, = 1.0 per unit Calculate: 1. Subtransient current in the generator 2. Symmetrical components of the voltage Vao, V.1 and Vaz from point a to ground