- 6 20 Pts A 20 Mva 13 8 Kv Generator Has The Following Data Subtransient Reactance 0 25 Per Unit Negative Sequence 1 (35.92 KiB) Viewed 11 times
#6 (20 pts): A 20 MVA, 13.8 kV generator has the following data: Subtransient reactance 0.25 per unit. Negative Sequence
-
- Site Admin
- Posts: 899603
- Joined: Mon Aug 02, 2021 8:13 am
#6 (20 pts): A 20 MVA, 13.8 kV generator has the following data: Subtransient reactance 0.25 per unit. Negative Sequence
#6 (20 pts): A 20 MVA, 13.8 kV generator has the following data: Subtransient reactance 0.25 per unit. Negative Sequence reactance: 0.35 per unit Zero Sequence reactance: 0.1 per unit. Internal voltage E, = 1.0 per unit Calculate: 1. Subtransient current in the generator 2. Symmetrical components of the voltage Vao, V.1 and Vaz from point a to ground