The 13.2kV-120/240 V distribution transformer that supplies a
residence suffers a breakdown during a storm and ends with the
neutral open. At a given moment the charges of the residence are
distributed as follows: L1: 1,450 W L2: 350W
If the house resistance 8 ohm, determine
The voltage between house neutral bus and the ground of the
transformer
The current through the body of a person that makes contact with
the house neutral and the ground 4500 ohm