Using a 100-MVA, 230 kV base for the TLs

Business, Finance, Economics, Accounting, Operations Management, Computer Science, Electrical Engineering, Mechanical Engineering, Civil Engineering, Chemical Engineering, Algebra, Precalculus, Statistics and Probabilty, Advanced Math, Physics, Chemistry, Biology, Nursing, Psychology, Certifications, Tests, Prep, and more.
Post Reply
answerhappygod
Site Admin
Posts: 899603
Joined: Mon Aug 02, 2021 8:13 am

Using a 100-MVA, 230 kV base for the TLs

Post by answerhappygod »

Using a 100-MVA, 230 kV base for the TLs
Using A 100 Mva 230 Kv Base For The Tls 1
Using A 100 Mva 230 Kv Base For The Tls 1 (36.99 KiB) Viewed 31 times
Using A 100 Mva 230 Kv Base For The Tls 2
Using A 100 Mva 230 Kv Base For The Tls 2 (95.4 KiB) Viewed 31 times
compute the fault currents and voltages at the fault for: (a) a bolted single line-to-ground fault at bus 3, (b) a bolted line-to-line fault at bus 3, (c) a bolted double line-to-ground fault at bus 3. Also, for the single line-to-ground fault at bus 3, determine the currents and voltages at the terminals of generators G1 and G2. Consider the effect of A-Y transformer phase shifts.
G1 ОН Gl G2 j0.03 Synchronous generators: 100 MVA 100 MVA Transformers: T1 T2 T1 100 MVA 100 MVA Transmission lines: TL12 100 MVA TL13 100 MVA TL23 100 MVA 25 kV 13.8 kV 230 kV 230 kV 230 kV TL13 3 TL12 25/230 kV 13.8/230 kV TL23 X₁ X₁ X₁ 2 X₁ X₂ = 0.2 X₁ = 0.05 X₁ = X₂ = 0.2 X = 0.05 T2 X₂ = 0.1 X₂ = 0.1 X₂ = 0.1 b HO A X₁ X₂ = Xo = 0.05 X₁ = X₂ = Xo = 0.05 Xo = 0.3 Xo = 0.3 Xo = 0.3 j0.03 G2
Join a community of subject matter experts. Register for FREE to view solutions, replies, and use search function. Request answer by replying!