Refer to the sample problem on Analysis of Beams Reinforced for Tension in the lesson module (b = 400 mm, d= 550 mm, 4-25 mm diameter rebars). Determine if the beam is safe using the "transformed section method" we recently discussed.
pls. refer to this problem
PROBLEM: For the reinforced concrete beam shown, determine the area of the steel ce inforcement for a balanced design. If so reinforced, determine the safe moment capacity of the section, f'c-20 MPa, fs = 140 MPa, n = 10 100 300 100 5:00 fc-9MPa 200 mm GOO M 80 60 144 Solution: NAS 500 mm fo - 0.45 fe fc 9 MPa 880-x 14 14x 880(9)-9x X -536 mm 5000) ( - 2000-2001 200)-As (880-x) 500(344)(2)-200x144) 10A (336) AI 5133 mm 100344) hp 880-X =14M₂ 1013 (06/
Moment capacity of concrete: MX fo B 1 M (344) (1000) 2 C 6 21332 x 10 Mc = 558 kN m Moment capacity of steel: M (880-x) fs 1 n 140 M (536X1000) S 10 21332 x 10 Ms = 558 KN mu Check: Moment capacity of steel must be equal to that of concrete for a balanced design Safe moment capacity 559 KN m 62
Refer to the sample problem on Analysis of Beams Reinforced for Tension in the lesson module (b = 400 mm, d= 550 mm, 4-2
-
- Site Admin