project statement
A double-ended switchgear is fed from 2 utility 2000 kVA
transformers during normal operating condition (Utility Mode), with
tiebreaker Normally Open. When Normal power is lost, a 2000 kVA
standby generator G1 feeds the left-side of the switchgear via an
Automatic Transfer Switch (ATS1), and another 2000 kVA generator G2
feeds the right side of the switchgear via ATS2. Tiebreaker between
the right side and the left side of the switchgear is Normally Open
during normal operation.
The following data is given below:
Utility data
Transformer data
Generator data
Feeders data
Panels data
Utility Utility ID UTIL-1 UTIL-2 Rated Voltage (V) SC Contribution 3P (Amps) 13800 5000.0 13800 5000.0 SC Contribution SLG (Amps) 4500.0 4500.0 X/R 3P X/R SLG 8.0000 8.0000 8.0000 8.0000
Cable Cable ID Voltage CBL-0001 13800.0 CBL-0002 480.0 CBL-0003 480.0 CBL-0004 480.0 CBL-0005 480.0 CBL-0006 480.0 CBL-0007 480.0 CBL-0008 208.0 CBL-0009 480.0 CBL-0010 480.0 CBL-0011 480.0 CBL-0012 480.0 CBL-0013 13800.0 CBL-0014 480.0 CBL-0015 480.0 CBL-0016 480.0 CBL-0017 480.0 CBL-0018 480.0 CBL-0019 480.0 CBL-0020 240.0 CBL-0021 480.0 CBL-0022 480.0 CBL-0023 480.0 CBL-0024 480.0 CBL-0025 277.0 CBL-0026 480.0 From Bus ID BUS-0001 T1-S Swgr- Bus-L SWBD S1 SWBD S1 SWBD $1 Swgr- Bus-L T3-S Swgr- Bus-L Swgr- Bus-L GEN1. BUS ATS1 BUS-0006 T2-S Swgr. Bus-R SWBD S2 SWBD S2 Swgr. Bus-R Swgr. Bus-R T5-S Swgr. Bus-R Swgr. Bus-R GEN2 BUS ATS2-E T4-S Swgr. Bus-R To Bus ID T1-P ATS1 N SWBD S1 PNL-A. PNL-B. M-1 T3-P PNL-C. M-2 M-3 ATS1 E Swgr- Bus-L T2-P ATS2-N SWBD S2 T4-P M-5 M-6 T5-P PNL-E. PNL-D. M-7 BUS-0027 Swgr. Bus-R M-4 BUS-0044 ConductorType Insulation Copper 100% THHN Copper Copper THHN Copper THHN Copper THHN Copper THHN Copper THHN Copper THHN Copper THHN Copper THHN Copper THHN Copper THHN Copper 100% Copper THHN Copper THHN Copper THHN Copper THHN Copper THHN Copper THHN Copper THHN Copper THHN Copper THHN Copper THHN Copper THHN Copper THHN Copper THHN Length (ft) 55.0 45.0 15.0 30.0 80.0 90.0 45.0 25.0 30.0 25.0 50.0 40.0 55.0 45.0 25.0 25.0 42.0 38.0 25.0 66.0 65.0 50.0 50.0 30.0 25.0 55.0 Qty Per Phase 1 6 2 1 3 1 1 2 1 2 5 5 1 6 3 2 1 1 1 2 1 1 5 7 3 2 Spring 2022 Size 1 500 600 1 2 250 350 500 400 400 750 750 1 500 400 400 500 500 3/0 3/0 2 2 750 600 500 350
Generator Data Component Subviews: Synchronous Generator ANSI Contribution Decrement Curve Harmonic Source Reliability Data User-Defined Fields Datablock Scenario Manager... Jump... Go To G Component Subviews: Synchronous Generator ANSI Contribution Decrement Curve Harmonic Source Reliability Data User-Defined Fields Datablock Scenario Manager... Jump... Go To G G1 In Service G Data State: Incomplete FLA: 2405.6 Synchronous rpm: 1800.00 Wye-Ground Name: G1 Rated Voltage: 480 V (L-L) Rated Size: 2000.000 KVA Power Factor: 0.900 Lag Poles: 4 -Initial Operating Conditions and Participation Factors- Schedule: Volts & Angle (SB) Angle: 0.00 Deg. Voltage: 1.000 pu Bus Connection Three Phase Bus: Connection... GEN1. BUS Single Phase Mid Tap Single Phase -Generator Contribution Data (ANSI Format) -Saturated Per Unit Impedance- Impedance Base Sequence X/R Ratio KVA Base: Positive: 0.1500 20.0000 Voltage Base: 480 Negative: 0.1500 20.0000 Zero: 0.1500 20.0000 ✔Link with Rated Typical R (Ohms) X (Ohms) Neutral Impedance: 0.0000 0.0000 Calc... -Transient and Steady State Saturated Impedance and Parameters xd: 0.2900 xd: 2.7500 Ra |0.0072 Id": 26.00 ms Id": 420.00 Tdc: 93.00 ms 2000.0 ms
project statement A double-ended switchgear is fed from 2 utility 2000 kVA transformers during normal operating conditio
-