Business, Finance, Economics, Accounting, Operations Management, Computer Science, Electrical Engineering, Mechanical Engineering, Civil Engineering, Chemical Engineering, Algebra, Precalculus, Statistics and Probabilty, Advanced Math, Physics, Chemistry, Biology, Nursing, Psychology, Certifications, Tests, Prep, and more.
Post Reply
answerhappygod
Site Admin
Posts: 899604
Joined: Mon Aug 02, 2021 8:13 am

Problem 4. A 33 kV, three-phase, 45 MVA synchronous generator is connected to a 50 Hz infinite bus. The generator is sup

Post by answerhappygod »

Problem 4 A 33 Kv Three Phase 45 Mva Synchronous Generator Is Connected To A 50 Hz Infinite Bus The Generator Is Sup 1
Problem 4 A 33 Kv Three Phase 45 Mva Synchronous Generator Is Connected To A 50 Hz Infinite Bus The Generator Is Sup 1 (35.1 KiB) Viewed 29 times
Problem 4. A 33 kV, three-phase, 45 MVA synchronous generator is connected to a 50 Hz infinite bus. The generator is supplying rated power at 0.8 power factor lagging, if the synchronous armature has negligible resistance and reactance per phase of the generator is 100. Determine: a) The excitation voltage per-phase and the load angle b) The armature current, load angle and power factor when the generator output is reduced to 30 MW by reducing the turbine input c) The maximum power that the generator can deliver without losing synchronism, armature current and the power factor In parts a) and b) assume constant excitation. d) Determine the minimum excitation required for the generator to deliver rated output without losing synchronisation
Join a community of subject matter experts. Register for FREE to view solutions, replies, and use search function. Request answer by replying!
Post Reply