A single phase step down transformer, rated 320 kVA, 4800/240 V is tested for its internal parameters. During short circ

Posted: Wed Apr 27, 2022 6:16 pm
by answerhappygod
A Single Phase Step Down Transformer Rated 320 Kva 4800 240 V Is Tested For Its Internal Parameters During Short Circ 1
A Single Phase Step Down Transformer Rated 320 Kva 4800 240 V Is Tested For Its Internal Parameters During Short Circ 1 (85.43 KiB) Viewed 41 times
A single phase step down transformer, rated 320 kVA, 4800/240 V is tested for its internal parameters. During short circuit (SC) test, secondary terminals are short circuited and a test voltage applied on primary terminals. When 200 V is applied rated primary current is measured on primary terminals and power input is measured to be 3,2 kW. During open circuit (OC) test, both terminals are open circuited and a test voltage is applied on secondary terminals. When rated voltage of 240 V is applied to the secondary terminal, current and power inputs are recorded at secondary side are 12 A and 1,6 kW, respectively. a) Using SC test, calculate equivalent series R and X of the TR referred to primary side (neglect shunt elements) (10p) b) Using OC test, calculate equivalent shunt Rand X of the TR referred to primary side (neglect series elements) (10p) c) What is the efficiency of the transformer for a load of 256 kW at 0,8 pf lagging at rated voltage? (10p) Z1 = R + X im I lo 1 IT Im Vi ReijXm13 E Zn = Ry+jX2 12 E2 122 Equivalent circuit of a transformer Zei Rel + Xel Flac Vsc SC test cct - ref. to primary lo ict Ral Vi བམ འ ག་ Im 3jXml E E, V2 OC test cct-ref. to primary