Two 50 Hz generators A and B rated 600 MW and 500 MW are operating in parallel. The droop characteristics are 4.5% and 3
Posted: Fri Jul 08, 2022 6:21 am
Two 50 Hz generators A and B rated 600 MW and 500 MW are operating in parallel. The droop characteristics are 4.5% and 3%, respectively, from no load to full load. Assume that the generators are operated at 50 Hz at no load condition. How would the no load speed of the generators be adjusted if a load of 800 MW be shared equally? a) 0.6 Hz increase of the no load speed of Generator A. b) 0.6 Hz increase of the no load speed of Generator B. c) 0.6 Hz decrease of the no load speed of Generator A. d) 0.6 Hz decrease of the no load speed of Generator B.