Question 5 Return air at 25°C and fresh outdoor air at 35°C is mixed in an adiabatic mixing chamber. If 22% of the mixed

Posted: Fri Jul 08, 2022 5:49 am
by answerhappygod
Question 5 Return Air At 25 C And Fresh Outdoor Air At 35 C Is Mixed In An Adiabatic Mixing Chamber If 22 Of The Mixed 1
Question 5 Return Air At 25 C And Fresh Outdoor Air At 35 C Is Mixed In An Adiabatic Mixing Chamber If 22 Of The Mixed 1 (51.47 KiB) Viewed 50 times
Question 5 Return air at 25°C and fresh outdoor air at 35°C is mixed in an adiabatic mixing chamber. If 22% of the mixed air is from outdoor air, what is the temperature of the mixed air in °C? A) 28.7 °C B) 22.7 °C C) 27.2 °C Question 6 Air with dry-bulb of 21°C flowing through a duct at 0.55 kg/s is sensibly cooled to 19°C. Assuming that cooling section is insulated and air is cooled using a chilled water, what is the required mass flow rate in kg/s of the chilled water if its allowable temperature rise is 5°C? (A) 0.054 kg/s B) 0.045 kg/s (C) 0.034 kg/s