Warm water enters a cooling tower at 36°C at a mass flow rate of 57.3 kg/s. The air entering at state 1 has h₁ = 53 kJ/k
Posted: Fri Jul 08, 2022 5:48 am
Warm water enters a cooling tower at 36°C at a mass flow rate of 57.3 kg/s. The air entering at state 1 has h₁ = 53 kJ/kg da and w₁ = 0.007 kg v/kg da. The air leaving the cooling tower at state 2 has h₂ = 104 kJ/kg da and w₂ = 0.028 kg v/kg da. The make up water is supplied at 25°C and the mass flow rate of dry air is 49.8 kg da/s. What is the temperature of the cooled water leaving the tower? Express your answer in °C.