As shown in the figure, an air conditioner operating at steady state maintains a dwelling at 70°F on a day when the outside temperature is 90°F. The rate of heat transfer into the dwelling through the walls and roof is 30,000 Btu/h and the net power input to the air conditioner compressor is 3 hp. Inside, 70° F Evaporator 30,000 Btu/h Refrigerant loop Compressor Outside Condenser Determine the coefficient of performance of the air conditioner. Determine the power input required, in hp, and the coefficient of performance for a reversible air conditioner providing the same cooling effect while operating between the same cold and hot temperatures.