Page 1 of 1

***Use LTspice for solved this problem only*** ***Use LTspice for solved this problem only*** ***Use LTspice for solved

Posted: Fri Jul 01, 2022 6:09 am
by answerhappygod
***Use LTspice for solved this problem only***
***Use LTspice for solved this problem only***
***Use LTspice for solved this problem only***
***Use LTspice for solved this problem only***
Use Ltspice For Solved This Problem Only Use Ltspice For Solved This Problem Only Use Ltspice For Solved 1
Use Ltspice For Solved This Problem Only Use Ltspice For Solved This Problem Only Use Ltspice For Solved 1 (285.48 KiB) Viewed 25 times
***Use LTspice for solved this problem only***
***Use LTspice for solved this problem only***
***Use LTspice for solved this problem only***
***Use LTspice for solved this problem only***
56. A transformer whose nameplate reads 2300/230 V, 25 kVA operates with primary and secondary voltages of 2300 V and 230 V rms, respectively, and can supply 25 kVA from its secondary winding. If this transformer is supplied with 2300 V rms and is connected to secondary loads requiring 8 kW at unity PF and 15 kVA at 0.8 PF lagging, (a) what is the primary current? (b) How many kilowatts can the transformer still supply to a load operating at 0.95 PF lagging? (c) Verify your answers with PSpice.