b) Real power P, = 2050 kW at 0.8 lagging power factor is provided to the sending end of the single-phase transmission l

Posted: Thu Jun 02, 2022 8:55 am
by answerhappygod
B Real Power P 2050 Kw At 0 8 Lagging Power Factor Is Provided To The Sending End Of The Single Phase Transmission L 1
B Real Power P 2050 Kw At 0 8 Lagging Power Factor Is Provided To The Sending End Of The Single Phase Transmission L 1 (62.39 KiB) Viewed 25 times
b) Real power P, = 2050 kW at 0.8 lagging power factor is provided to the sending end of the single-phase transmission line in Figure 1. The line impedance is Z = 0.5 + j0.5, and the voltage across the load VŔ is 3 kV. Calculate the load (in kW), load power factor as well as the supply voltage V. [4 Marks] Z-R+jX I VR P Vs Figure 1: Single-phase transmission line