Formwork is needed for an 8-ft high concrete wall. The concrete will be internally vibrated and poured at a rate of 8.5
Posted: Sat May 21, 2022 2:47 pm
Formwork is needed for an 8-ft high concrete wall. The concrete will be internally vibrated and poured at a rate of 8.5 th at a temperature of 95°F The sheathing will be Class 1 Plywood 4 x 8 sheets, %-inch thick The studs and double wales will be 2 x 4 Douglas Fir with the following properties Fb = 1910 psi Fv = 110 psi FC = 455 psi E 17 xtos The deflection must not exceed U240 Assuming that the stud spacing, as calculated is 12 inches, determine the design load and the spacing of the Wales