(a) When the system is filled (at 35°C ambient temperature) it is desired to have a pressure of 70 kPa at the highest po
Posted: Sat May 21, 2022 9:06 am
(a) When the system is filled (at 35°C ambient temperature) it is desired to have a pressure
of 70 kPa at the highest point in the system which will reduce to 35 kPa when the water
temperature reduces to 7°C.
(b) What operating pressures (p1, p2) should the expansion tank be designed for? What
pump head is required?
(c) With the pump off and a cold (7°C) system, what is the pressure at the pump suction?
The pump discharge?
(d) With the pump on and a cold (7°C) system, what is the pressure at the pump suction?
The pump discharge?
(e) “Engineers considered chilled water system is a closed-loop system. Pipe and pump
design need not to consider static pressure head”. Based on the above calculation, comment
whether this statement correct or not.
In a chilled-water system, the pump is located in a basement equipment room with the expansion tank connected to the pump suction. The pump is the lowest point in the system and the highest point is a pipe in the penthouse, which is 50m above the pump. The dynamic head losses in the system are: Table A3 Head loss in pipes Piping and fittings 10m Chiller 6m Control valve 3m Cooling coil 4m (a) When the system is filled (at 35°C ambient temperature) it is desired to have a pressure of 70 kPa at the highest point in the system which will reduce to 35 kPa when the water temperature reduces to 7°C. (b) What operating pressures (p1, p2) should the expansion tank be designed for? What pump head is required? (c) With the pump off and a cold (7°C) system, what is the pressure at the pump suction? The pump discharge? (d) With the pump on and a cold (7°C) system, what is the pressure at the pump suction? The pump discharge? (e) "Engineers considered chilled water system is a closed-loop system. Pipe and pump design need not to consider static pressure head". Based on the above calculation, comment whether this statement correct or not.
of 70 kPa at the highest point in the system which will reduce to 35 kPa when the water
temperature reduces to 7°C.
(b) What operating pressures (p1, p2) should the expansion tank be designed for? What
pump head is required?
(c) With the pump off and a cold (7°C) system, what is the pressure at the pump suction?
The pump discharge?
(d) With the pump on and a cold (7°C) system, what is the pressure at the pump suction?
The pump discharge?
(e) “Engineers considered chilled water system is a closed-loop system. Pipe and pump
design need not to consider static pressure head”. Based on the above calculation, comment
whether this statement correct or not.
In a chilled-water system, the pump is located in a basement equipment room with the expansion tank connected to the pump suction. The pump is the lowest point in the system and the highest point is a pipe in the penthouse, which is 50m above the pump. The dynamic head losses in the system are: Table A3 Head loss in pipes Piping and fittings 10m Chiller 6m Control valve 3m Cooling coil 4m (a) When the system is filled (at 35°C ambient temperature) it is desired to have a pressure of 70 kPa at the highest point in the system which will reduce to 35 kPa when the water temperature reduces to 7°C. (b) What operating pressures (p1, p2) should the expansion tank be designed for? What pump head is required? (c) With the pump off and a cold (7°C) system, what is the pressure at the pump suction? The pump discharge? (d) With the pump on and a cold (7°C) system, what is the pressure at the pump suction? The pump discharge? (e) "Engineers considered chilled water system is a closed-loop system. Pipe and pump design need not to consider static pressure head". Based on the above calculation, comment whether this statement correct or not.