Ex.5: Estimate the sensible and latent cooling load in a building due to ventilation and infiltration if a ventilation r
Posted: Sat May 21, 2022 1:56 am
Ex.5: Estimate the sensible and latent cooling load in a
building due to ventilation and infiltration if a ventilation rate
of 7 L/s per person is selected as representative of a drugstore or
hardware store. With 85 people, the total ventilation air quantity
is thus 595 L/s. infiltration due to wall cracks, window
untightened seal, and frequent door opening is assumed to be 31
L/s. Assume: 1. outdoor design conditions: Dry bulb = 35°C, wet
bulb = 25°C; 2. indoor design conditions. Dry bulb = 24°C, wet bulb
= 18°C