The no-load voltage of a three phase, 60 Hz, Y-connected synchronous generator is 3464 V. When the generator delivers th

Posted: Fri May 20, 2022 11:40 pm
by answerhappygod
The No Load Voltage Of A Three Phase 60 Hz Y Connected Synchronous Generator Is 3464 V When The Generator Delivers Th 1
The No Load Voltage Of A Three Phase 60 Hz Y Connected Synchronous Generator Is 3464 V When The Generator Delivers Th 1 (30.52 KiB) Viewed 16 times
The no-load voltage of a three phase, 60 Hz, Y-connected synchronous generator is 3464 V. When the generator delivers the rated load of 432 kW at 0.8 pf lagging, the terminal voltage is 3117.69 V. If the armature winding resistance is 0.2 Ohm/phase, determine the synchronous reactance of the generator and the power angle. When the load is changed to 80 + j60 Ohm/phase, determine the terminal (line) voltage.