) For a 50 Hz, 1000 kVA, 11kV/380V three-phase transformer, the short-circuit test carried out at the high voltage side

Posted: Sun May 15, 2022 2:17 pm
by answerhappygod
For A 50 Hz 1000 Kva 11kv 380v Three Phase Transformer The Short Circuit Test Carried Out At The High Voltage Side 1
For A 50 Hz 1000 Kva 11kv 380v Three Phase Transformer The Short Circuit Test Carried Out At The High Voltage Side 1 (59.58 KiB) Viewed 70 times
) For a 50 Hz, 1000 kVA, 11kV/380V three-phase transformer, the short-circuit test carried out at the high voltage side (with the low voltage side short-circuited) has a multi-wattmeter reading of 18 kW and a voltmeter reading of 660 volts (line-to-line) when the input current is at rated level. Estimate: (i) The equivalent impedance of the transformer referred to high voltage side and low voltage side, respectively; (ii) The voltage regulation of the transformer at a load power factor of 0.80 lagging. (15 marks)