• An electrical engineer tested a 50 kVA, 1000/250 V, 50 Hz, single-phase transformer, and the test results are given in

Posted: Mon May 09, 2022 7:53 am
by answerhappygod
An Electrical Engineer Tested A 50 Kva 1000 250 V 50 Hz Single Phase Transformer And The Test Results Are Given In 1
An Electrical Engineer Tested A 50 Kva 1000 250 V 50 Hz Single Phase Transformer And The Test Results Are Given In 1 (76.08 KiB) Viewed 24 times
• An electrical engineer tested a 50 kVA, 1000/250 V, 50 Hz, single-phase transformer, and the test results are given in Table Bl. Test Voltage Current Power 250 V 5A 200 W Open-circuit test (Low Voltage Side Measurement) Short-circuit test (High Voltage Side Measurement) 90 V 50A 1800 W Table B1 By using an approximate equivalent circuit, evaluate (a) the equivalent core loss resistance and magnetizing reactance referred (6 marks) to high voltage side, (b) the equivalent winding resistance and flux leakage reactance referred (3 marks) to high voltage side, (c) the voltage regulation at 75% full load and 0.8 power factor lagging, (6 marks) and (d) the output power at maximum efficiency, (5 marks)