current under the new conditions. Neglect losses. [268 V; 6", 20.6 A] 5. A 400-V, 3-phase, Y-connected synchronous motor
Posted: Thu May 05, 2022 2:35 pm
No.5 please correct answer
current under the new conditions. Neglect losses. [268 V; 6", 20.6 A] 5. A 400-V, 3-phase, Y-connected synchronous motor takes 3.73 kW at normal voltage and has an impedance of (1 +j8) ohm per phase. Calculate the current and p.f. if the induced e.m.f. is 460 V. [6.28 A; 0.86 lead] (Electrical Engineering, Madras Univ. April 1979) -C00
current under the new conditions. Neglect losses. [268 V; 6", 20.6 A] 5. A 400-V, 3-phase, Y-connected synchronous motor takes 3.73 kW at normal voltage and has an impedance of (1 +j8) ohm per phase. Calculate the current and p.f. if the induced e.m.f. is 460 V. [6.28 A; 0.86 lead] (Electrical Engineering, Madras Univ. April 1979) -C00